F2 is low pressure protection. Suction pressure fell below what the system needs and it stopped rather than run the compressor at a temperature it cannot survive. Low pressure narrows to two things on most Carrier systems: not enough refrigerant in the circuit, or not enough heat being picked up because airflow across the indoor coil is restricted.
Less gas in the circuit means less to compress, so suction pressure falls until protection opens. Refrigerant does not get used up on a sealed system, so a shortfall is a leak by definition. A unit that needs gas each season is telling you it has one, and the pressure test finds it rather than another top up.
The usual locations are flare joints, brazed connections, Schrader cores and the coil itself. Vibration, poor brazing and corrosion each take their turn, and some leaks only show once the system is hot. An electronic detector finds most of them, and a nitrogen pressure test confirms the ones that hide.
A sensor can report low pressure on a system holding correct charge, which is why the reading is always cross-checked against a gauge on the same port. A sensor that does not follow the gauge is the fault. Replacing it is far cheaper than a recharge that was never needed in the first place.
Suction pressure and superheat are measured together and compared with the manufacturer’s figures for the outdoor temperature. If the charge is short, the leak search happens before any gas goes in. Refilling without that step simply resets the clock on the next F2 trip.
Every joint is checked with an electronic detector, with flares and Schrader cores getting particular attention because they fail most often. Where nothing shows, the circuit is pressure tested with nitrogen and left to stand. The drop proves a leak, and the detector finds where it is.
The sensor is tested against a gauge on the same service port. A reading that diverges, or one that stays flat while pressure changes, confirms the sensor. The plug and lead are checked at the same time, because a poor connection produces exactly the same symptom at no cost to fix.